I'm helping another member with a unit that has 26 hours after CECOM rebuild, that can not hold 8kw load before an overload fault. It will hold 8kw for approximately 15 minutes, then 10-12kw for 5 minutes before the overload trip. Cleaned the S8 and S6 extensively, swapped K8, checked burden resistors and traced wires with the same results. One item I have noticed is that the burden resistors get extremely hot (burn your fingers) within 3 minutes at 10kw, before the overload trips.