Mep-803 -S1 switch broke

gonzo119

New member
6
5
3
Location
San Juan, PR
S1 switch broke while in prime and run position. Tried to use a pair of pliers to start but the plastic is too worn. Pushed in the emergency stop switch to stop the fuel prime. Any ideas on how to start? Will dead crank start?
thank you!
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,800
5,848
113
Location
MA
If Jaime doesn't have any spare S1s, I do. Good luck getting it going right now.

If your switch is stuck at the prime and run position, you could probably mechanically hold open the fuel shutdown solenoid (zip tie, etc) while using the dead crank to get it going, and quickly flip the dead crank back to normal operation.
 
Last edited:

kloppk

Well-known member
Steel Soldiers Supporter
2,126
3,492
113
Location
Pepperell, Massachusetts
If S1 is still in Prime/Run you ought to be able to start it using the dead crank switch and manually moving the Fuel Solenoid.
Pull out the Emergency Off button. Let fuel pump run for about 15 seconds.
With one hand fully retract the Fuel Solenoid and hold it there. With the other hand put the Dead Crank Switch in the Crank position. After the engine starts move the Dead Crank Switch to the NORMAL position. Then let go of the Fuel Solenoid. It ought to stay retracted and the engine should continue to run.
Assuming the gen head has enough residual magnetism the gen head should begin to produce electricity.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,800
5,848
113
Location
MA
If S1 is still in Prime/Run you ought to be able to start it using the dead crank switch and manually moving the Fuel Solenoid.
Pull out the Emergency Off button. Let fuel pump run for about 15 seconds.
With one hand fully retract the Fuel Solenoid and hold it there. With the other hand put the Dead Crank Switch in the Crank position. After the engine starts move the Dead Crank Switch to the NORMAL position. Then let go of the Fuel Solenoid. It ought to stay retracted and the engine should continue to run.
Assuming the gen head has enough residual magnetism the gen head should begin to produce electricity.
You beat my edit (y)
 

kloppk

Well-known member
Steel Soldiers Supporter
2,126
3,492
113
Location
Pepperell, Massachusetts
Another method is this, assuming S1 is in Prime/Run.
Pull out the Emergency Off button. Let fuel pump run for about 15 seconds.
Use a jumper wire to touch S1 terminals 3 & 7. This is the equivalent of moving S1 to the Start position.
Once the set starts and oil pressure comes up remove the jumper. This method will flash the gen head to cause it to make power in case adequate residual magnetism is gone.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,800
5,848
113
Location
MA
Another method is this, assuming S1 is in Prime/Run.
Pull out the Emergency Off button. Let fuel pump run for about 15 seconds.
Use a jumper wire to touch S1 terminals 3 & 7. This is the equivalent of moving S1 to the Start position.
Once the set starts and oil pressure comes up remove the jumper. This method will flash the gen head to cause it to make power in case adequate residual magnetism is gone.
Yeah always good to know the shortcuts. For those who are unaware, the pinout on the S1 is located in the -24 wiring layout. Attached below:

Untitled.png
 

gonzo119

New member
6
5
3
Location
San Juan, PR
S1 switch broke while in prime and run position. Tried to use a pair of pliers to start but the plastic is too worn. Pushed in the emergency stop switch to stop the fuel prime. Any ideas on how to start? Will dead crank start?
thank you!
Thank you! Appreciate everyone’s help!! The jumper wires did the trick! Spoke to Jmenede about getting the replacement and spare parts. Thanks again to everyone. 🙏🏻
 

Glenn H

Member
24
18
18
Location
Virginia
Another method is this, assuming S1 is in Prime/Run.
Pull out the Emergency Off button. Let fuel pump run for about 15 seconds.
Use a jumper wire to touch S1 terminals 3 & 7. This is the equivalent of moving S1 to the Start position.
Once the set starts and oil pressure comes up remove the jumper. This method will flash the gen head to cause it to make power in case adequate residual magnetism is gone.
@kloppk, I am in need of your expertise, Ray70 mentioned you in my thread, “Mep 803a won’t shut off”, I had Injector problems that we got taken care of, but did not know I needed a fuse on the Quad windings ( I will put a fuse in between the quad winding pens, can you tell me what fuse I need to place there?) Before I repaired the IP’s I had 240 volts on my volt meter, after the repair and start up the engine problem was solved but I no longer have voltage, I had to wind the starter longer than normal because the pumps were dry from being repaired, any help would be much appreciated. Thanks to you and Roy70
 

kloppk

Well-known member
Steel Soldiers Supporter
2,126
3,492
113
Location
Pepperell, Massachusetts
@kloppk, I am in need of your expertise, Ray70 mentioned you in my thread, “Mep 803a won’t shut off”, I had Injector problems that we got taken care of, but did not know I needed a fuse on the Quad windings ( I will put a fuse in between the quad winding pens, can you tell me what fuse I need to place there?) Before I repaired the IP’s I had 240 volts on my volt meter, after the repair and start up the engine problem was solved but I no longer have voltage, I had to wind the starter longer than normal because the pumps were dry from being repaired, any help would be much appreciated. Thanks to you and Roy70
I just replied to your thread on the problem of no power with your set. You'll need to do some voltage checks so we can narrow down the problem.
Per the field sustsinment bulletin a FNQ-R-3 fuse is required. I have kits available for the modification with all the parts and instructions.

Kurt
 

Glenn H

Member
24
18
18
Location
Virginia
I just replied to your thread on the problem of no power with your set. You'll need to do some voltage checks so we can narrow down the problem.
Per the field sustsinment bulletin a FNQ-R-3 fuse is required. I have kits available for the modification with all the parts and instructions.

Kurt
How do I get one of your kits?
 

Guyfang

Moderator
Staff member
Moderator
16,676
23,822
113
Location
Burgkunstadt, Germany
Glenn,

You need to try and keep your keep all your stuff in one thread. You could have gotten the same help, just by posting in your OTHER thread. If you start posting all over, in 2-or more threads, the same problem, its counter productive. To much info, scattered in too many threads. This thread is about S1 problems.
 

Glenn H

Member
24
18
18
Location
Virginia
Glenn,

You need to try and keep your keep all your stuff in one thread. You could have gotten the same help, just by posting in your OTHER thread. If you start posting all over, in 2-or more threads, the same problem, its counter productive. To much info, scattered in too many threads. This thread is about S1 problems.
Sure will , I’m not sure how this thread got started, must have been something I did unknowingly. Thanks for the help.
 

Glenn H

Member
24
18
18
Location
Virginia
Sure will , I’m not sure how this thread got started,
Glenn,

You need to try and keep your keep all your stuff in one thread. You could have gotten the same help, just by posting in your OTHER thread. If you start posting all over, in 2-or more threads, the same problem, its counter productive. To much info, scattered in too many threads. This thread is about S1 problems.
oh yes I see what you are saying, sorry Thanks for the help.
 