You know, wire 137N goes from S-1, pin 3 to TB6-4.

Splits off, and one wire goes to M5, (fuel indicator) neg side.

Another wire goes from the TB6-4 to J3, (diagnostic cannon plug) pin r.

And the last wire goes to TB5-11, then on to P4-14 on the A2 (malfunction indicator). Could the fault indicator be bad? Back feeding that wire?

Or is M5 wired wrong? There is after all, 4 wires on M5.
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,532
2,059
113
Location
Efland, NC
I'm trying to figure the best route to eliminate A2. Since I don't know all the failure modes for that device I'm just guessing. If CB1 shuts it down it we may be looking at a power leak on A2. If CB1 shuts it down the next step will be to lift the wire going to Term 4 on A2.

So far I feel reasonably good about eliminating Term3 of S1 and eliminating the starting circuit from the leak.

Now to work around the other side of the B+ circuit (A2).

What has me puzzled is why E-Stop didn't shut it down. That is going to be the same thing as pulling CB1.

An interesting puzzle.
 

Triton

Active member
240
81
28
Location
Houston, Texas
I was able to check CB1 before going to work this am, I started the unit and turned S-1 to off then pulled CB1, it didn't turn off. I did try starting the unit with CB-1 pulled out and it would not start.
 

Triton

Active member
240
81
28
Location
Houston, Texas
I rechecked tonight Pin N and no voltage with the switch in off position, Pin K and Pin R have 24 volts in off position. I rechecked and activated CB1 in the off position and it didn't shut off the system. Thanks for the correct pin out document, I enlarged that so I could read a lot easier.
 

Guyfang

Moderator
Staff member
Moderator
16,755
24,058
113
Location
Burgkunstadt, Germany
If the wire is on the wire terminal, it could be back feeding to the wire going to S-1, pin 3. You said that wire was hot when disconnected from S-1. Also, pin r on the J3 diagnostics canon plug is hot with the S-1 turned off. That's not right. I explained it in message # 81. The voltage is supposed to COME from S-1, and go outwards. If A2 is no longer in the equation, then there are only a few other places to check.
 

Triton

Active member
240
81
28
Location
Houston, Texas
Pin R on the J3 diagnostics canon plug is hot with the S-1 turned off when the engine is running, when I pull the fuel solenoid to shut off the motor it goes to 0 volts.
I checked the wires on both sides of TB6-4, they are correct, 137-N, 137-F on one side and 137-A and 137-U on the other side.
Also M-5 was correct with 128-B on S terminal and 137-H and 137-F on I terminal, 100AR was ground
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,532
2,059
113
Location
Efland, NC
Do you know which relay is K16?

I would like you to start the unit then turn S1 to OFF. Next, remove K16 from its socket.

See if it shuts down.
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,532
2,059
113
Location
Efland, NC
Ok. This should do it then. Disconnect all the wires from the alternator and make sure they aren't touching anything. I think either your regulator is bad or someone wired up the alternator wrong. Don't let any of the wires touch either other. Start it up then try to shut it down with S1.
 