Hello everyone and thank you in advance for any advice provided. I'm a new member to this site but have been reading many older posts for a while now in an attempt to get my generator running.
I recently purchased a MEP-803a generator that was in a half disassembled state. The previous owner had passed away and his wife was selling the unit. He clearly had it connected to power his home before. It came with a brand new main stator, still in the box. The guy was very meticulous about labeling every wire connection, so it only took me about an hour and a half to get the unit up and running, but it produced no power. So, assuming he ordered correct part that the machine needed, I swapped out the stator. The unit still won't produce power. I have scoured through the manuals and run many tests. Near as I can figure, the exciter rotor is bad. I am only getting 1.8 volts at terminals 5 + 6 on voltage regulator. According to manual I should have 8, some posts here have indicated 6. The bearing clearly went bad on end of gen rotor at some point and new bearing doesn't seat correctly. I've fixed that, but now think the rotor rubbed the exciter stator and did damage to itself. Not all of the leads on exciter rotor test out correctly with ohm meter. The generator stator and rotor did test correctly, so I am attempting to get some sort of power out of the unit before spending $1000 on the exciter rotor. The original main stator also tested correctly, so I don't think that was even a problem, but now it has the brand new one installed.
It did take me a while to figure out that I needed to hold start position to energize the field.
Here are my current questions: When I hold start to energize field, I can clearly see a heavy drain on the engine side of 24v electrical system. What I can't tell is what is causing that draw and where that power is being directed. The voltage regulator has no different power at any time. I've seen it actually lose power when start is held and drop down to half a volt. Only 2x out of the probably 50 or so times I've started the unit did I see the frequency hertz meter read anything. And it only did so for a few seconds then quit working. Does the frequency meter work all the time? Or only after the generator field is activated? It is more like an rpm gauge, or truly just for the electrical half of the system? The "test" for the frequency transducer has you check OHMs at the Hertz meter, so that does me no good. How else can I check the frequency transducer? The 2x the frequency hertz meter did actually work, the unit still showed no power on voltage output gauge.
I took a 6 volt lantern battery and ran it direct to terminals 5 + 6 in an attempt to create the voltage needed at terminals, and I still did not get any output from generator. One post I read here stated if the generator q1 and q2 had power sent to it, it should generate power regardless if voltage regulator is working or not. I don't have correct voltage at any terminals on voltage regulator. Not even close to correct readings on any terminals.
When I plug a drill into the convenience outlet. There is a small amount of power, but only enough to make the drill groan. I show 8 volts at the output side of the voltage regulator.
I purchased a new field flash module as original one looked toasted inside. Clearly had a burnt diode. Switching that out has made no difference. Any ideas?
One last question. There is this square box looking thing about 2.5" x 2.5" that has (had) four wires coming out of it. It seems like it was connected with, or near, the electric fuel pump somehow. It has been bypassed. It is mounted on the inside left side door, but I'm not certain that was original location for it. What should it do? The unit also has brand new 12v fuel pump in it somehow. I thought these all had 24V fuel pumps?
I've modified the generator end housing to accept a wider bearing to correct the issue the previous owner had, but would like to replace housing completely. Once I determine I can get this unit to make power, where might I be able to find the end housing? I've searched several sites and can't find anything available anywhere.
Thanks again for all your help in advance.
I recently purchased a MEP-803a generator that was in a half disassembled state. The previous owner had passed away and his wife was selling the unit. He clearly had it connected to power his home before. It came with a brand new main stator, still in the box. The guy was very meticulous about labeling every wire connection, so it only took me about an hour and a half to get the unit up and running, but it produced no power. So, assuming he ordered correct part that the machine needed, I swapped out the stator. The unit still won't produce power. I have scoured through the manuals and run many tests. Near as I can figure, the exciter rotor is bad. I am only getting 1.8 volts at terminals 5 + 6 on voltage regulator. According to manual I should have 8, some posts here have indicated 6. The bearing clearly went bad on end of gen rotor at some point and new bearing doesn't seat correctly. I've fixed that, but now think the rotor rubbed the exciter stator and did damage to itself. Not all of the leads on exciter rotor test out correctly with ohm meter. The generator stator and rotor did test correctly, so I am attempting to get some sort of power out of the unit before spending $1000 on the exciter rotor. The original main stator also tested correctly, so I don't think that was even a problem, but now it has the brand new one installed.
It did take me a while to figure out that I needed to hold start position to energize the field.
Here are my current questions: When I hold start to energize field, I can clearly see a heavy drain on the engine side of 24v electrical system. What I can't tell is what is causing that draw and where that power is being directed. The voltage regulator has no different power at any time. I've seen it actually lose power when start is held and drop down to half a volt. Only 2x out of the probably 50 or so times I've started the unit did I see the frequency hertz meter read anything. And it only did so for a few seconds then quit working. Does the frequency meter work all the time? Or only after the generator field is activated? It is more like an rpm gauge, or truly just for the electrical half of the system? The "test" for the frequency transducer has you check OHMs at the Hertz meter, so that does me no good. How else can I check the frequency transducer? The 2x the frequency hertz meter did actually work, the unit still showed no power on voltage output gauge.
I took a 6 volt lantern battery and ran it direct to terminals 5 + 6 in an attempt to create the voltage needed at terminals, and I still did not get any output from generator. One post I read here stated if the generator q1 and q2 had power sent to it, it should generate power regardless if voltage regulator is working or not. I don't have correct voltage at any terminals on voltage regulator. Not even close to correct readings on any terminals.
When I plug a drill into the convenience outlet. There is a small amount of power, but only enough to make the drill groan. I show 8 volts at the output side of the voltage regulator.
I purchased a new field flash module as original one looked toasted inside. Clearly had a burnt diode. Switching that out has made no difference. Any ideas?
One last question. There is this square box looking thing about 2.5" x 2.5" that has (had) four wires coming out of it. It seems like it was connected with, or near, the electric fuel pump somehow. It has been bypassed. It is mounted on the inside left side door, but I'm not certain that was original location for it. What should it do? The unit also has brand new 12v fuel pump in it somehow. I thought these all had 24V fuel pumps?
I've modified the generator end housing to accept a wider bearing to correct the issue the previous owner had, but would like to replace housing completely. Once I determine I can get this unit to make power, where might I be able to find the end housing? I've searched several sites and can't find anything available anywhere.
Thanks again for all your help in advance.