• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP 804A RETAPPING

jamawieb

Well-known member
1,437
556
113
Location
Ripley/TN
Do you have a link to where you previously discussed your conversions?
Let me see if I can find it. It wasn't a thread I started. The idea came from SmokeStak where an individual talked about a Bar Diamond connection. Worked on the theory with some other guys and it worked. The only set back we had was the VR. The original VR reads off all 3 legs to generate power. With Kurt Klopp's VR development, it was a game changer because his VR on reads off of 1 leg. So with the conversion, you have to put in Kurts VR, the remaining conversion is completed on the reconnection board. Its actually easier to do than the older 004 and 005 models. I have logged several thousand hours on 804s so the conversion is very dependable.
 

2Pbfeet

Well-known member
434
773
93
Location
Mt. Hamilton, CA
Let me see if I can find it. It wasn't a thread I started. The idea came from SmokeStak where an individual talked about a Bar Diamond connection. Worked on the theory with some other guys and it worked. The only set back we had was the VR. The original VR reads off all 3 legs to generate power. With Kurt Klopp's VR development, it was a game changer because his VR on reads off of 1 leg. So with the conversion, you have to put in Kurts VR, the remaining conversion is completed on the reconnection board. Its actually easier to do than the older 004 and 005 models. I have logged several thousand hours on 804s so the conversion is very dependable.
Are the threads by WA Ross? E.g.

He seems very confident of his views, and they seem supported by diagrams that don't look crazy to me, but I am not an electrical engineer. He does point out the 1/3 loss in KVA capacity.

All the best,

2Pbfeet
 

jamawieb

Well-known member
1,437
556
113
Location
Ripley/TN
Are the threads by WA Ross? E.g.

He seems very confident of his views, and they seem supported by diagrams that don't look crazy to me, but I am not an electrical engineer. He does point out the 1/3 loss in KVA capacity.

All the best,

2Pbfeet
That is one of the articles. I shared the conversion with Peter who owns Innovahightech because he was very confident that it could NOT be done. He contacted electrical engineers with Marthon and explained the conversion, to his surprise they confirmed the ability with my drawings. Rated output of the generator is still 15kw on the 804 and 30kw on the 805. But anything over that trips the overload. Usually on the 804 I can push them until 19-20kw before overload happens.
 

2Pbfeet

Well-known member
434
773
93
Location
Mt. Hamilton, CA
That is one of the articles. I shared the conversion with Peter who owns Innovahightech because he was very confident that it could NOT be done. He contacted electrical engineers with Marthon and explained the conversion, to his surprise they confirmed the ability with my drawings. Rated output of the generator is still 15kw on the 804 and 30kw on the 805. But anything over that trips the overload. Usually on the 804 I can push them until 19-20kw before overload happens.
Thanks for the deep due diligence on your and Peter's (@peapvp) part! It is nice to know that on the 804/805 sets that there is no loss in capacity.

All the best,

2PbFeet
 

peapvp

Well-known member
Steel Soldiers Supporter
1,118
1,244
113
Location
Basehor, KS
That is one of the articles. I shared the conversion with Peter who owns Innovahightech because he was very confident that it could NOT be done. He contacted electrical engineers with Marthon and explained the conversion, to his surprise they confirmed the ability with my drawings. Rated output of the generator is still 15kw on the 804 and 30kw on the 805. But anything over that trips the overload. Usually on the 804 I can push them until 19-20kw before overload happens.
@jamawieb
I am getting old, when did I have this conversation with you and Marathon(?)
I can’t remember this conversation and just checked my email archives and my steelsoldiers pm
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks