• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

Mep-804B help?

stag0608

New member
4
5
3
Location
Boutte, La
Guy’s I have a problem. My generator will not stay running. It is cutting out on no fuel. The thing is that’s it full of fuel, and fuel gauge showing full also. Do y’all think the float may be stuck? Haven’t had a chance to dig into it yet.
 
Last edited:

Ray70

Well-known member
2,582
5,860
113
Location
West greenwich/RI
Take a look at the 804 TM , it uses a similar Dual float / Float Control module arrangement as the 802 / 803 does.
The issue is most likely either with the lower float ( possibly stuck ) on item 62 or an issue with the float module, item 71
But check the TM, I'm familiar with that issue on the 802/803 but not sure off hand if the 804 uses the exact same
 

loosegravel

Just a retired mechanic who's having fun!
504
891
93
Location
Enumclaw, Washington
I thought that the MEP-804A and B models have a mechanical fuel lift pump when running off of the main tank? I believe the only electric pump on those models is used for auxiliary fuel supply, unless I’m mistaken. But I suppose that they still have a shut-down for low fuel? In that case a faulty low fuel signal could actually be your problem. But I do believe that these models are known for losing their prime though. Leaky fuel supply lines can allow the fuel to return to the tank while sitting, causing the starting and stalling scenario at first start-up. You won’t see any external fuel leakage.
 

Ray70

Well-known member
2,582
5,860
113
Location
West greenwich/RI
I believe ( or I thought ) what he meant is the machine is shutting itself off ( electronically ) due to a ( false ) Low Fuel indicator.
If that is correct, the issue is somewhere in the low fuel circuit, most likely either the float or the float module.
I don't think he is saying the machine is stalling due to a lack of fuel at the injectors.
 

loosegravel

Just a retired mechanic who's having fun!
504
891
93
Location
Enumclaw, Washington
I believe ( or I thought ) what he meant is the machine is shutting itself off ( electronically ) due to a ( false ) Low Fuel indicator.
If that is correct, the issue is somewhere in the low fuel circuit, most likely either the float or the float module.
I don't think he is saying the machine is stalling due to a lack of fuel at the injectors.
You’re probably correct. His post was kind of vague. It didn’t say that he was getting a low fuel fault, but that’s more than likely what it is.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks