Hello everyone,
im pretty new here but have adsorbed and found a tremendous amount of information here to troubleshoot my 804B. Just a quick background on the set.
2010 MEP 804b with 185 hours on it, bought it at auction. Engine wouldn't start when i first started working on it and discovered a missing MPU. After installing a replacement and adjusting it, the engine fire right up. The under voltage light comes on as soon as i let go of S1. I proceed with the troubleshooting section in the TM with section 4-2.1 for internal crack relay test. This passed. Then moved on to section 4-1.2 for the voltage regulator and it failed. ( I have the fuse mod) Here's what i've got
4-1.2 Testing (AC Voltage Regulator, P/N 01-21501-2, for MEP-804A/MEP-804B).
h. Set multimeter for DC volts and connect positive lead to wire 141A. Connect negative lead of
multimeter to terminal 3 of AC voltage regulator. Start generator set and operate at rated
frequency. Move and hold MASTER SWITCH in START position. Multimeter should indicate
between 4 and 12 VDC.
I have anywhere between 18-22VDC here
j. Set multimeter for AC volts and connect to terminals 10 and 11 of AC voltage regulator. Start
generator set and operate at rated frequency. Move and hold MASTER SWITCH in START
position. Multimeter should indicate 110 to 160 VAC.
Im only getting 7 VAC
l. Disconnect wire 137A from terminal 5 of AC voltage regulator. Set multimeter for ohms and
connect positive lead to wire 137A and negative lead to terminal 4 of AC voltage regulator. Move
VOLTAGE adjust potentiometer to full CCW position. Multimeter should indicate no more than 2
ohms with FREQUENCY SELECT switch in 60 Hz position or 50 Hz position. Move VOLTAGE
adjust potentiometer slowly CW while observing multimeter. Multimeter should increase smoothly
to approximately 20,000 ohms
Im getting an open circuit here
i would assume that the voltage regulator is fried and i will take a look at that later, what i have an issue with is that im getting 18-22 VDC on terminal 1 and 3 when it should be 4-12. After doing some more research in the forum, this appears to be the flashing circuit? I went on and performed the following test posted by guyfang in another thread
All this is with S1 held in start position
1. measure dc voltage at S1 terminal 7. Should read 24 VDC. 24 VDC
2. measure dc voltage at CR4 terminal 1 and 2. should read 24VDC. 24VDC
3. measure dc voltage at R14 terminal 1 . Should read 24 VDC. 24VDC
4. measure dc voltage at R14 terminal 2. Should be between 5-11VDC. 18VDC
5. measure dc voltage at CR2 terminal 1. Should be between 5-11VDC. 17VDC
6. measure dc voltage at CR2 terminal 1. Should be between 5-10VDC. 18VDC
Since im getting more voltage in step 4 on r14 terminal 2, i would assume that (resistor?) is bad? I do get a 40 ohm reading.
Tested most of the resistors and it looks like r10,11 and 12 are blown. i get maybe 1 ohm and it looks like they're 7.5 ohm resistors. Any idea what might have caused this? I don't want to throw money at a new regulator if i have a much bigger issue somewhere.
im pretty new here but have adsorbed and found a tremendous amount of information here to troubleshoot my 804B. Just a quick background on the set.
2010 MEP 804b with 185 hours on it, bought it at auction. Engine wouldn't start when i first started working on it and discovered a missing MPU. After installing a replacement and adjusting it, the engine fire right up. The under voltage light comes on as soon as i let go of S1. I proceed with the troubleshooting section in the TM with section 4-2.1 for internal crack relay test. This passed. Then moved on to section 4-1.2 for the voltage regulator and it failed. ( I have the fuse mod) Here's what i've got
4-1.2 Testing (AC Voltage Regulator, P/N 01-21501-2, for MEP-804A/MEP-804B).
h. Set multimeter for DC volts and connect positive lead to wire 141A. Connect negative lead of
multimeter to terminal 3 of AC voltage regulator. Start generator set and operate at rated
frequency. Move and hold MASTER SWITCH in START position. Multimeter should indicate
between 4 and 12 VDC.
I have anywhere between 18-22VDC here
j. Set multimeter for AC volts and connect to terminals 10 and 11 of AC voltage regulator. Start
generator set and operate at rated frequency. Move and hold MASTER SWITCH in START
position. Multimeter should indicate 110 to 160 VAC.
Im only getting 7 VAC
l. Disconnect wire 137A from terminal 5 of AC voltage regulator. Set multimeter for ohms and
connect positive lead to wire 137A and negative lead to terminal 4 of AC voltage regulator. Move
VOLTAGE adjust potentiometer to full CCW position. Multimeter should indicate no more than 2
ohms with FREQUENCY SELECT switch in 60 Hz position or 50 Hz position. Move VOLTAGE
adjust potentiometer slowly CW while observing multimeter. Multimeter should increase smoothly
to approximately 20,000 ohms
Im getting an open circuit here
i would assume that the voltage regulator is fried and i will take a look at that later, what i have an issue with is that im getting 18-22 VDC on terminal 1 and 3 when it should be 4-12. After doing some more research in the forum, this appears to be the flashing circuit? I went on and performed the following test posted by guyfang in another thread
All this is with S1 held in start position
1. measure dc voltage at S1 terminal 7. Should read 24 VDC. 24 VDC
2. measure dc voltage at CR4 terminal 1 and 2. should read 24VDC. 24VDC
3. measure dc voltage at R14 terminal 1 . Should read 24 VDC. 24VDC
4. measure dc voltage at R14 terminal 2. Should be between 5-11VDC. 18VDC
5. measure dc voltage at CR2 terminal 1. Should be between 5-11VDC. 17VDC
6. measure dc voltage at CR2 terminal 1. Should be between 5-10VDC. 18VDC
Since im getting more voltage in step 4 on r14 terminal 2, i would assume that (resistor?) is bad? I do get a 40 ohm reading.
Tested most of the resistors and it looks like r10,11 and 12 are blown. i get maybe 1 ohm and it looks like they're 7.5 ohm resistors. Any idea what might have caused this? I don't want to throw money at a new regulator if i have a much bigger issue somewhere.