Mep-805a- 30kw generator

walkerman

New member
17
6
1
Location
Palm Harbor florida
need help the overspeed and under voltage light stay on and will not run cleaned sensor and still did not work . will a new one help ? do not have part number

anyone in the Clearwater Florida area that works on these need to find someone

Thank you
 

Tinstar

Super Moderator
Super Moderator
Steel Soldiers Supporter
4,290
1,776
113
Location
Edmond, Oklahoma
Welcome to Steel Soldiers

Have you downloaded the Technical Manual?
Did you search the forums for the same issue?
Issue has most likely been covered before.
 

Suprman

Well-known member
Supporting Vendor
6,861
696
113
Location
Stratford/Connecticut
The tms are in the section top of the forum page. There are step by step troubleshooting. If you download them and start troubleshooting, and still get stuck, you can at least post how far you got in the process. Making it easier for someone to offer advice.
 

Guyfang

Moderator
Staff member
Moderator
16,766
24,082
113
Location
Burgkunstadt, Germany
need help the overspeed and under voltage light stay on and will not run cleaned sensor and still did not work . will a new one help ? do not have part number

anyone in the Clearwater Florida area that works on these need to find someone

Thank you
Lets start again. Did this gen set ever work right? Is it new to you? Did you reset the fault indicator?
 

Guyfang

Moderator
Staff member
Moderator
16,766
24,082
113
Location
Burgkunstadt, Germany
You have to reset the over speed first, then the fault indicator. Is that how you did it? If not, or if you cant remember, re do it.
 

Guyfang

Moderator
Staff member
Moderator
16,766
24,082
113
Location
Burgkunstadt, Germany
Try this. Reset the fault indicator, and hold it in the reset position. Then start the set. Keep the fault indicator in reset position. Then flip up the battle short switch. THEN let the reset go. Still running?
 

walkerman

New member
17
6
1
Location
Palm Harbor florida
Thank You I will try it Monday I'm in Florida looking at the weather. I'm in Clearwater Fl and if anyone knows someone near me that works on these generators I would be happy to pay someone to help.
 

mcii

New member
72
2
0
Location
Wimberley, Texas
also ? DOESN'T THIS SERIES HAVE THE overspeed RESET LOLCATED ON OR WITHIN THE INTERIOR OF THE CONTROL BOX NEXT TO THE 50/60 SELECTOR SWITCH.. DONT THINK JUST PUSHING THE TESTLAMP RESET BUTTON ON THE INDICATOR PANEL ON THE FRONT PANEL WILL ACTUALLY RESET THE OVERSPEED CONDITION.. LET US KNO MAC/MC
 

walkerman

New member
17
6
1
Location
Palm Harbor florida
Thank You I got the generator running most problem were dirty connections. I need to find out how to make this 3 phase generator to
single phase I watched Matt Verley u-tube on doing a mep-oo4A generator I would like to find out if this is the same
Thank You
 

Scoobyshep

Well-known member
1,137
1,511
113
Location
Florida
The 005 is a 12 lead head, so he did a retap to low zigzag. If memory serves the 805 is a 10 lead head and cant be changes the same way.
 

Guyfang

Moderator
Staff member
Moderator
16,766
24,082
113
Location
Burgkunstadt, Germany
Thank You I got the generator running most problem were dirty connections. I need to find out how to make this 3 phase generator to
single phase I watched Matt Verley u-tube on doing a mep-oo4A generator I would like to find out if this is the same
Thank You

Ain't gonna happen. You are talking about apples, (MEP-805A), Matt is talking about pears, (MEP-005A).
 