So the placard states that 3 phase adjustment range is 60hz 395-480v. So ....I ass u me.... that means i can run a 480v Y load using this machine?
When I fire it up and begin adjusting voltage up, I get an "overvoltage" message at about 457v. The bar graph stops at 430v. But it will climb to 480v and beyond. This gives me a 277v L1 to L0 voltage. 480v L1 to L2 as measured.
Should (can) I disregard the overvoltage warning. Again specs state adjustable range of 395-480. Will this compromise the machine in anyway?
I am looking to use it to power a 3○ robotic demolition machine.
Thank you