MEP 805B Voltage out of synch

SteveTheGreen

Member
54
5
8
Location
Oklahoma
One generator ran well for a week. Then phase 1 got out of synch with the other two phases. Double. Phase 1 is 214, b and c are 107.
I swapped out a good voltage regulator. No change. Sometimes it will fix itself. Any ideas?

Sent from my SM-G960U using Tapatalk
 

Scoobyshep

Well-known member
963
1,096
93
Location
Florida
Do you have a load applied? Check your neutral, ground, and the bond in-between.

Sent from my SM-G973U using Tapatalk
 