This is all great info. Thank you, guys.
I am having a problem with my 831A. The engine is running well. However, it will only charge the lugs in when I activate (Battle Short) and then close the interrupter. If I start the unit and try to set the interrupter without the Battle short on, the lugs will not charge.
Any ideas?
Recommend starting a new thread. It will be better for us to help you.
 

MarauderPPK

New member
4
0
1
Location
Deutschland
my MEP-831A runs good when it runs, but it has a bad startup issue. Preheating up to 45 seconds didn't make a difference. I was sick about the bad startups and thought the fuel is running backwards. But every manual startup attempt was a very successful attempt with no issues at all so i am wondering more and more... months over months are gone... the comparision to a construction machine's diesel engine or a mower was the forewarding idea: first we open the gas throttle to idle speed, then we crank the engine. The magnetic actuator is held by the magnet to close the throttle to stop the engine. But it is held during startup and after cranking a long minute it release and then the engine can run (!) - what is defective on the controller? Is there a relay contact worn? Or is this a problem of the controller (he must give a current on the coil of the actuator on RUN-Position to immediate release the actuator from the magnet, but it won't work)? When i pull it manually away from the magnet, it starts up on starter position immediately with no issues as like in manual startup procedure. Had you found a healthy solution for this (i don't want to pull the actuator off the magnet manually every startup; because i want to let a plc decide to autostart up and stop the genset).
 

kloppk

Well-known member
Steel Soldiers Supporter
2,145
3,526
113
Location
Pepperell, Massachusetts
The 831 SLC100 Governor Controllers (GC) are extremely failure prone. That's why I make and sell a reliable replacement.
When you move S1 from STOP to RUN the GC is supposed to put out a brief pulse of power to the actuator to pop it off the magnet. Very likely it's the GC that failed. Another slim possibility is that someone fiddled with the strength of the magnet and made it too strong.
 