I'm evaluating getting a generator to run a grain bin that I'm putting up this summer vs having REC drop electric for me - getting a quote from them this next week I hope.
Just considering the option that a GL MEP 004/005?? might be viable option to power the site instead (no recuring monthly charges).
Loads: 10 hp centrifugal fan - would be running by itself for the most part other then maybe some block heaters at the same time I think during harvest. the 10 hp fan could be ordered as a single or three phase fan. The other loads would be a 7.5 hp unload auger and beyond that maybe a 10 hp electric unload belt that could run at the same time - but that could be a pto powered unit potentially.
Run time continuous would be 7-10 days straight right at harvest to initally dry, otherwise some intermitant times during the year spring and fall for block heaters and the unload.
Any input as to a MEP 004 15KW being large enough? or would a 005 / 30KW be the need? Also - any ideas on fuel consumption for these motors?
other question would be - if wired for three phase for smaller wires, cheaper motor, easier starting - would the other (smaller) 7.5 or 5hp motors need to be 3phase as well? or could they be run single with the generator? Or would that be too unbalanced ? I assume a person could pull 5kw or under single phase while it was setup for 3phase without any issue?
Thanks for your input and knowledge.
Just considering the option that a GL MEP 004/005?? might be viable option to power the site instead (no recuring monthly charges).
Loads: 10 hp centrifugal fan - would be running by itself for the most part other then maybe some block heaters at the same time I think during harvest. the 10 hp fan could be ordered as a single or three phase fan. The other loads would be a 7.5 hp unload auger and beyond that maybe a 10 hp electric unload belt that could run at the same time - but that could be a pto powered unit potentially.
Run time continuous would be 7-10 days straight right at harvest to initally dry, otherwise some intermitant times during the year spring and fall for block heaters and the unload.
Any input as to a MEP 004 15KW being large enough? or would a 005 / 30KW be the need? Also - any ideas on fuel consumption for these motors?
other question would be - if wired for three phase for smaller wires, cheaper motor, easier starting - would the other (smaller) 7.5 or 5hp motors need to be 3phase as well? or could they be run single with the generator? Or would that be too unbalanced ? I assume a person could pull 5kw or under single phase while it was setup for 3phase without any issue?
Thanks for your input and knowledge.