I'm in need of a replacement 24v Solid State Regulator FVR 4006 for my mep002 generator.
Does anyone have a source for these?
Thanks.
Does anyone have a source for these?
Thanks.
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!
...
I replaced the Voltage Regulator with a tested used one. Running at the fuse 0.47 amps ac where it should be 6.5 amps..."when loaded by a discharged battery". ...
As far as I know there is no alternator on this unit.A/C? Not DC? The only place (that I know of, but don't have one of this model) were there would be A/C is the stator output. If you had a defective stator diode(s), you might have A/C on the output, likely low current, and no charging.
Thanks - AC I believe is correct.
Have you checked the alternator's rectifiers to be sure they are OK? If not, I'll make that my WAG...
Well it's going to be something simple like this - I hope - but I did tripple check myself on the meter setting - I appreciate it .... keep em coming.Do you have your meter set right? I remember when I was trying to sort my charging system out I was trying to read D/C when I had my meter set on A/C (which didn't work out so well).
Just sayin...
Just a suggestion, double check your stator output again. That would be the wire #1 and #2 you refer to above. When running you should be somewhere in the neighborhood of 33 volts or so (with one meter lead on wire 1 and one on wire 2, set for AC volts). If you have 33 volts and the fuse and fuse holder are both good, then you have a bad VR. Whether they said it was good or not, it sure sounds bad to me.I retested the Voltage Regulator. Results:
@ fuse not running. No ac or dc present.
@ fuse running. ac volts 0.42. ac amps 0. dc 0.
Testing the 3 bottom wires. Left to right.
not running Wire #1. No ac or dc present.
running Wire #1. ac volts 8.0. ac amps 0. dc 4.3.
not running Wire #2. No ac or dc present.
running Wire #2. ac volts 1.9. ac amps 0. dc 0.7.
not running Wire #3 w/red band. ac volts 0. ac amps 0. dc 24.6.
running Wire # 3 w/red band. ac volts 0. ac amps 0. dc 24.3.
"Running" is at 1,800 rpm with no load. Tested with a Fluke 322 meter.
I'm open to any ideas. Thanks, David
I've also seen strange things with fuses that seemed good, and were not. I always try to test by replacing (was taught that in the military!) and not testing. Some people look at a fuse and say "it is good" as if a visual inspection tells them something--not a chance, I've seen so many that were open at the far end, under the end caps where it was not visible....
Just a side note...I have never seen it happen on a small glass fuse, but I have seen it on larger 30 amp cartridge fuses on a 250 VDC system, we've had some "Partially" blown fuses where I work, and make troubleshooting a royal pain. The fuses would show continuity with a meter, and show voltage passing through them, but as soon as any kind of amperage tried to pass they would open up. Remove the load and your are back to normal showing continuity and voltage again. As I said though, I've never seen anything like that on a small glass fuse.
Bill, My original fuse holder was questionable as the metal ring on the outside of the housing was a little loose. Last week I went to Granger and picked up another. The replacement is not as the original in that it does not mount to the backing plate. It's just an in line fuse holder currently hanging out the front side of the backing plate.Did you check the fuse holder? My fuse was good but the spring wire inside the fuse holder was bad and not making contact with the fuse, Just throwing it out there
On the fuses I put in a new one this morning before I tested above. The fuse is a BUSS AGC 15 AMP 32 V.Just a suggestion, double check your stator output again. That would be the wire #1 and #2 you refer to above. When running you should be somewhere in the neighborhood of 33 volts or so (with one meter lead on wire 1 and one on wire 2, set for AC volts). If you have 33 volts and the fuse and fuse holder are both good, then you have a bad VR. Whether they said it was good or not, it sure sounds bad to me.
Speddmon, Retested this morning: Running at 1800rpm I got 33.2 ac volts.
Not running 0.6 ohms to 0.7 ohms.
Test at the fuse holder was 0.42 ac volts.
Just a side note...I have never seen it happen on a small glass fuse, but I have seen it on larger 30 amp cartridge fuses on a 250 VDC system, we've had some "Partially" blown fuses where I work, and make troubleshooting a royal pain. The fuses would show continuity with a meter, and show voltage passing through them, but as soon as any kind of amperage tried to pass they would open up. Remove the load and your are back to normal showing continuity and voltage again. As I said though, I've never seen anything like that on a small glass fuse.
PeterD, That was a creative solution for testing. I would need to take some time and work on new skills to pull it off. Another member went with a 75-TVA1343 from Mouser.Com. But it is out of the given spec range. In case my copy paste does not work, the difference is the Mouser unit is 100volt, not 75 volt. Is the difference enough to keep looking? Thanks, DavidIf that is the specifications, then...
Two of these, wired in series (to get above the 75 volt specification) would work for a test if nothing else. 100µF 50V 20% Radial-lead Electrolytic Capacitor - RadioShack.com
Just watch the polarity when you wire them up.
No, after I saw it was broken I did not go further. Installing it I was not comfortable with how I had to bend the wires to mount it on the backing plate and make the connections.Buy it...the voltage rating is basically just the maximum voltage the capacitor will handle without breaking down. You could probably get by with a 50 volt cap, but if there are any spikes induced by the generator portion (which is why that cap is there to begin with) they could easily be over 50 volts.
So, when you put the old one back on did it fix your problem?? I can't imagine that it would have, but I am very curious.