Ive been repairing my mep003a recently. It was producing electricity as it should and then I moved the unit from the truck to trailer. I went to start up the unit the other day and now while having the selector on 120/240 volts, the voltage gauge was reading 140 volts. I tested the lugs and L1 showed 70 volts and L3 showed 70 volts. Convenience outlet also showed 70 volts. So I dug into the TMs and followed the procedure on paragraph 8-2 in TM5-6115-585-34 to supply 12 volts at TB3-5 and TB3-6. After a few seconds of the unit running with the 12 volts supplied, the voltage meter jumped up and then started to swing from 190V to 260V. I let it run for 15 seconds and then shut it down. Looked over everything and tried again. Voltage still swings from 190 to 260. The link shows a video of the gauge swinging. No audible sound of loading and unloading of the motor. I checked the lugs to confirm the reading and my fluke meter did bounce back and forth. Just want to see what this could be? I am not an electrical engineer, so Im trying to learn as I go.
Video - https://www.youtube.com/watch?v=SCrPaRGQuBs
Video - https://www.youtube.com/watch?v=SCrPaRGQuBs