OK, I am confused. In your first post you said you had an MEP-006 Generator. Stonepicker1 referenced you to a TM that is for an MEP-806A. The similarities are about the same as corn flakes and moonbeams. So what generator do you have? Because you need to use the manuals and schematics.
The 120 volt outlets have a circuit breaker. CB-2 if I remember right. Is that tripping? Or is CB-1, the main control panel circuit breaker? We need more detailed info. I worked this model generator for a number of years.
Does your Hertz meter work? If not, you can check the function of the Frequency transducer, (the box that makes the freq. meter work) and find out if the transducer or meter is bad.
The 120 volt outlets have a circuit breaker. CB-2 if I remember right. Is that tripping? Or is CB-1, the main control panel circuit breaker? We need more detailed info. I worked this model generator for a number of years.
Does your Hertz meter work? If not, you can check the function of the Frequency transducer, (the box that makes the freq. meter work) and find out if the transducer or meter is bad.