The MEP 804A in stock form is only made to produce three phase power. This does not mean that single phase is not available. TM
9-6115-643-10 shows in Table 1 on pg 0005-4 how to do it. I remember reading somewhere in a TM about the 804A where it also talks about getting single phase power out to be sure and balance the loads on the diferent phases to avoid damage. This is different than the threads that describe how to modify the reconnection board to get single phase power. In the 120/208 reconnection board setting, 120 v single phase power is available L1, L2,
or L3 to L0. 208v is available L1-L2, etc. If you need 240v, the reconnection board setting must be changed to 240/416.
Then, 240v is L1-L0, etc. If you do this too hard on one phase, without balancing the load on other phases, damage to the gen head may result according to the TM.
Robert