Was able to fire up an MEP4 (ASK model) this evening. (Sorry no photos yet...late night & have to travel a few days this week).... Here's the basic report:
Engine was found with oil & filter & full coolant & both fuel filters. Filled tank with my standard mix of
TC3 O/B oil, fuel additive & diesel & then primed the fuel system & had the unit running in short order. No fault indicators, good frequency, oil pressure DC charging good. A couple issues showed up on the gauge board as follows:
1. AC voltmeter is "stuck" on 120, regardless of the selector switch setting.
2. Courtesy outlet functions properly (ran a 1500 watt heater but did not measure voltage).
3. Main circuit breaker switch seems to not function (no amber indicator light up when pushed up)..
4. With the main circuit breaker pushed up (closed position) I get ~240v at each of the three output lugs.
It seems the generator is working OK but I need to sort out the voltmeter or selector switch malfunction. Any ideas anyone?
Thanks,
Kevin
Engine was found with oil & filter & full coolant & both fuel filters. Filled tank with my standard mix of
TC3 O/B oil, fuel additive & diesel & then primed the fuel system & had the unit running in short order. No fault indicators, good frequency, oil pressure DC charging good. A couple issues showed up on the gauge board as follows:
1. AC voltmeter is "stuck" on 120, regardless of the selector switch setting.
2. Courtesy outlet functions properly (ran a 1500 watt heater but did not measure voltage).
3. Main circuit breaker switch seems to not function (no amber indicator light up when pushed up)..
4. With the main circuit breaker pushed up (closed position) I get ~240v at each of the three output lugs.
It seems the generator is working OK but I need to sort out the voltmeter or selector switch malfunction. Any ideas anyone?
Thanks,
Kevin