The generator runs through about 50 ft of 8 guage to the panel, then it is another 50ft of 10g out to the pump.
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!
You are using 8AWG for a 3000 watt generator? way overkill but shouldnt be an issue.The generator runs through about 50 ft of 8 guage to the panel, then it is another 50ft of 10g out to the pump.
240V I think. But it is 120/240 split type. There is a switch inside you change. The panel switches just change the output to the gauges.You are using 8AWG for a 3000 watt generator? way overkill but shouldnt be an issue.
out of curiosity what do you have the voltage set at? or is it non adjustable.
Yes this. If you have a voltage adjust and you are on the low side you may be seeing excessive drop. you can safely run at 125/250 volt (doesnt seem like much but it might be just enough to kick the motor over)He means what voltage do you have the Voltage Adjust knob at.
You should be able to set the output to anything from 220-250V
Not sure what your typical well repair service situation is in CT but "Dependable's recommendation" to replace a 35 yr old pump sounds like good advice. Better to have a preemptive plan to avoid an emergency "well out no water" situation due to eventual end of life pump failure unscheduled situation.
I just went through that last year at my barn/shop well. A long frustrating story with unfortunate sequence of events that I will spare the details, but there are now smart pump motors out there that don't require a contol box only the pressure switch circuit that controls power on/off.
I installed an intelligent 3-wire Grundfos 3" submersible pump (they also offer larger diameter ones as well as 2 wire with ground models) that have built in protections including overload, dry run, soft start and does not require a control box. Due to my shop well being at lower elevation of my property and only ~75' deep I downsized from the original old 3/4 hp pump to a 1/2 hp and it has performed excellent in the 6 months since installation and is more efficient running.
In the owners manual it has a section on "Generator Operation" and the 1/2 HP 3 wire 240 volt is 1200 W minimum and 1500 W recommended. The 3/4 HP model is 1900 W minimum and 2500 W recommended generator size.
Anyway, just passing on some info for your reference/consideration.