First time poster and long time reader. Have several other model MEPs and pieces of military equipment, and not afraid to get my hands dirty.
I recently acquired an MEP-804A, after changing batteries and a new alternator, it is still showing an under voltage warning light at all times when running.
Batteries were bad and was not charging before, is charging now.
The under voltage light is on at all times when running. When in the start position, it creates a little over 200 volts per gauge and drops to zero when you let off S1. Fuse is good and tested for ohms.
I ran through TM 9-6155-645-24 section 2-55 and when i run it with the wire from terminal 5 on the voltage regulator disconnected, it does not shut off and the gauges were identical from before disconnecting it. Also tried disconnecting the warning light harness with no change as far as i can tell.
Should I continue to look at replacing the Over/Under voltage relay, or look towards testing the voltage regulator or MPU testing/adjusting?
Been reading through here and the TMs just trying to get a more experienced opinion before replacing the over/under voltage relay or voltage regulator
I recently acquired an MEP-804A, after changing batteries and a new alternator, it is still showing an under voltage warning light at all times when running.
Batteries were bad and was not charging before, is charging now.
The under voltage light is on at all times when running. When in the start position, it creates a little over 200 volts per gauge and drops to zero when you let off S1. Fuse is good and tested for ohms.
I ran through TM 9-6155-645-24 section 2-55 and when i run it with the wire from terminal 5 on the voltage regulator disconnected, it does not shut off and the gauges were identical from before disconnecting it. Also tried disconnecting the warning light harness with no change as far as i can tell.
Should I continue to look at replacing the Over/Under voltage relay, or look towards testing the voltage regulator or MPU testing/adjusting?
Been reading through here and the TMs just trying to get a more experienced opinion before replacing the over/under voltage relay or voltage regulator