Unused wires on mep 803a

SalmonSlayer

Member
36
16
8
Location
Alaska
Just curious if one was only using the gen on single phase 120/240 if any of the wires on the big ass switch on the back wall can be eliminated for simplicity. Same for the AM/VM switch on the front. ( I want to say s7 but could be wrong). Keep getting short circuit alarm when it rains and I spray them both with deoxit and cycle switches which does seem to help but if I decided to take it all apart and clean it thoroughly I wondered if any of the wires could be omitted
Thanks
 

Digger556

Well-known member
Steel Soldiers Supporter
268
608
93
Location
Denver CO
There is a lot that COULD be eliminated. The engine is very basic at its core, requiring only pressurized fuel and and a quick spin (starter) to get it running.

The gen-head is a standard 12 wire with a field coil. The 12 wires could be permanently wired in 120/240v configuration. You could bypass the CTs, the contactor, the mode switch etc., it is just a matter of looking at the wiring diagrams to understand HOW to bypass those components.

Same goes for the AM/VM switch. You could hardwire an output directly to the volt meter or from the CT to the load meter.
 

2Pbfeet

Well-known member
433
773
93
Location
Mt. Hamilton, CA
Just curious if one was only using the gen on single phase 120/240 if any of the wires on the big ass switch on the back wall can be eliminated for simplicity. Same for the AM/VM switch on the front. ( I want to say s7 but could be wrong). Keep getting short circuit alarm when it rains and I spray them both with deoxit and cycle switches which does seem to help but if I decided to take it all apart and clean it thoroughly I wondered if any of the wires could be omitted
Thanks
I agree with @Guyfang on this one as well. Unless you go all in, stripping this down to an engine and a gen head with AVR, you are going to have a lot of wires, so the odds that removing the wires will solve the short issue is much less than one in three in my book. If you want a stripped down generator, why not swap this one for one built that way?

Personally, I'd spend the effort double checking terminal cleanliness, screw tightness, wire integrity, getting vibrating wires away from metal, and giving every single conductor end a shot of De-Oxit, not just the switches, though that's great too.

You didn't mention where in Alaska you are, so this is just a guess. If your generator is in a damp area, or an area exposed to humidity, like being on damp soil, there is going to be condensation on metal surfaces such as terminal strips and switches. A residual coating of De-Oxit will help keep water off the wires and contacts. Even better would be getting the generator under cover, and in an insulated enclosure.

All the best,

2Pbfeet
 

Ray70

Well-known member
2,598
5,926
113
Location
West greenwich/RI
I'm not all that well versed in how the burden resistors work, but I think there could also be a possibility of a damaged or cracked resistor, or a poor solder joint on one of them that could be causing your issue, if Detoxit in the switches isn't helping at all.
@kloppk is 100X better at explaining the resistor / overload / short circuit function than I am....
 

kloppk

Well-known member
Steel Soldiers Supporter
2,149
3,536
113
Location
Pepperell, Massachusetts
Since you are experiencing "SHORT CIRCUIT" I suspect @Ray70 suspicion or something like it may be causing the faults.
From the symptoms it sounds like it might be a bad connection or cracked resistor.

A short circuit fault gets tripped when the K8 Overload/Short Circuit relay thinks there is a SHORT CIRCUIT condition.
Details in a bit..

For each leg of the genset there is essentially a CT and Burden resistor which generate an AC voltage proportional to the load on each leg.
Each of teh 3 voltages are supplied to K8 so it can monitor for any Overload or Short Circuit conditions
Normally the AC voltage generated is between 0 and 5.6 volts AC. This represent 0 to 100% load on the corresponding leg.
At 133% Load the AC voltage is 7.5 volts.
A load of 130% will cause K8 to trigger an Overload after 8 +/- 2 minutes. If the overload is greater than 130% K8 will trigger an Overload fault quicker.
The time delay of the overload fault is inversely proportional to the amount of overload.

A SHORT CIRCUIT fault is triggered when sensed CT voltage is 23.9 volts, which is way more than the 7.3 volts of a minor overload.

The voltages above are generated by the CT and Burden resistor circuit. The CT outputs an AC Current which gets applied across the Burden resistor. That resulting current flow across the resistor creates the AC voltage across the resistor that K8 monitors.

If a Burden resistor or associated wiring, connectors or switch contacts result in the Burden resistors resistance to no longer be in parallel with the CT the resulting voltage will skyrocket causing K8 to throw a Short Circuit fault.

Here is a diagram showing the interconnect of the CT's and the Burden resistors. It does not show specifically all the wires and connectors that connect everything together. With the set in 120/240 mode CT3 gets both R12 and R13 applied in parallel across CT3 by way of a set of contacts in S8.

1722017588239.png
 

Guyfang

Moderator
Staff member
Moderator
16,790
24,135
113
Location
Burgkunstadt, Germany
On several sets I found that the Short Circuit fault light on, and it was the wires to the burden resisters in the left rear corner of the control cube. They had worn through, due to vibrations, against the side of the control cube. I like to look for shorts by opening all doors and take off the top of the gen set. Wait until dark and start the set up. In the dark. Look for a faint spark.
 

SalmonSlayer

Member
36
16
8
Location
Alaska
Wow lots of information to take in here. Thanks.
i know some of you have seen my other posts but I’ll recap a little. I’m using this generator to run a small salmon processing plant ( lighta, battery chargers, water pump, a couple vacuum packers, and a freezer). Everything works great most of the time. But occasionally when the freezer compressor kicks on everything goes out and I run to check the generator and it’s showing the short circuit light. I reset and energize the circuit again and everything works just fine until the freezer tries to kick on. This also usually happens when it’s been raining and we may not have gotten the door closed. The generator is inside a shed we made but it’s got a big sliding door in front. Occasionally the front of the unit gets rained on. We can work for weeks with no issue that’s why I was wondering if it was a moisture issue on the switch.This last time it happened I powered down and ran my backup generator and a couple hours later sprayed some deoxit and the 803 ran everything perfectly again
 

2Pbfeet

Well-known member
433
773
93
Location
Mt. Hamilton, CA
Wow lots of information to take in here. Thanks.
i know some of you have seen my other posts but I’ll recap a little. I’m using this generator to run a small salmon processing plant ( lighta, battery chargers, water pump, a couple vacuum packers, and a freezer). Everything works great most of the time. But occasionally when the freezer compressor kicks on everything goes out and I run to check the generator and it’s showing the short circuit light. I reset and energize the circuit again and everything works just fine until the freezer tries to kick on. This also usually happens when it’s been raining and we may not have gotten the door closed. The generator is inside a shed we made but it’s got a big sliding door in front. Occasionally the front of the unit gets rained on. We can work for weeks with no issue that’s why I was wondering if it was a moisture issue on the switch.This last time it happened I powered down and ran my backup generator and a couple hours later sprayed some deoxit and the 803 ran everything perfectly again
That is helpful.

Have you looked at how much your freezer actually draws when it kicks on? (LRA?) At first glance, since you have observed that it correlates with the freezer starting, I would at least consider that the LRA plus the other loads is too much, triggering the "Short circuit", rather than being certain it is water. Have you looked into perhaps getting a variable speed control for the freezer? They aren't always available, but they keep the freezer running more or less continuously in a shift, and allow for low current starts.

If you have some around, I would think about an inner vinyl door just to keep rain out for when folks forget to shut the door. Sliding door closers are, in my experience fiddly.

All the best,

2Pbfeet
 

jamawieb

Well-known member
1,437
556
113
Location
Ripley/TN
I dont think you have an issue with the generator. It sounds like the freezer is drawing way more than the generator can handle. The in rush of the compressor is causing the short circuit.
 

CallMeColt

Well-known member
Supporting Vendor
1,026
1,476
113
Location
Wilson County, Texas
I dont think you have an issue with the generator. It sounds like the freezer is drawing way more than the generator can handle. The in rush of the compressor is causing the short circuit.
An overload is not the same as a short circuit & will not cause this. Sounds like the freezer or the rain is bringing to surface a wire short issue.
 