• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

***URGENT*** MEP 803a set-up question ***SOLVED***

Islandfarmer

Member
22
31
13
Location
sw Florida
Hi folks,

I live on wiped out Pine Island in sw Florida courtesy of Hurricane Ian.
Just finished setting up my generator.
Would like you guys to sign off on what you see in the attached pics.
For some reason I think I saw somewhere the bar on the bottom right having to be removed when running the gen on 240 Volt?

Please lmk, thank you. 👍20221011_123708.jpg20221011_123734.jpgk y
 

peapvp

Well-known member
Steel Soldiers Supporter
1,159
1,344
113
Location
Basehor, KS
How are you feeding in to your House?
did you fully disconnect from the utility grid?
 

peapvp

Well-known member
Steel Soldiers Supporter
1,159
1,344
113
Location
Basehor, KS
Was any of your electrical wiring on wherever you are connecting to submerged in water / saltwater / brack water?

We need to see / know these things as well - this is a dremendous liability to advice someone in such a situation as this can potentially kill someone and or cause a fire
 

Guyfang

Moderator
Staff member
Moderator
17,492
25,873
113
Location
Burgkunstadt, Germany
The answer is no. What Peter is getting at, is the 1000 million Dollar question. Did you disconnect from the the grid? That determines what you need to do. Voltage has nothing to do with you question. And how did you disconnect it?
 

Islandfarmer

Member
22
31
13
Location
sw Florida
Was any of your electrical wiring on wherever you are connecting to submerged in water / saltwater / brack water?

We need to see / know these things as well - this is a dremendous liability to advice someone in such a situation as this can potentially kill someone and or cause a fire
Nothing was flooded here @ the house.
Had a 13kw Honda running the house but someone plugged in the hot tub and the Honda took some damage.
 

Evvy Fesler

Well-known member
366
772
93
Location
Roxboro, North Carolina USA
Hi folks,

I live on wiped out Pine Island in sw Florida courtesy of Hurricane Ian.
Just finished setting up my generator.
Would like you guys to sign off on what you see in the attached pics.
For some reason I think I saw somewhere the bar on the bottom right having to be removed when running the gen on 240 Volt?

Please lmk, thank you. 👍View attachment 881686View attachment 881687k y
You've got the right wire gauge... more than enough IAW NEC. I don't know what that strap does.
 

Islandfarmer

Member
22
31
13
Location
sw Florida
Added pictures

Main breaker is off.
Neutral and both phases in place on the outlet side.
Ground connected to 8' grounding rod.

A big Honda gen ran the house until last night but someone plugged in a hot tub and the Honda overloaded and took damage.

20221011_130034.jpg20221011_130039.jpg20221011_130053.jpg
 
Last edited:

Islandfarmer

Member
22
31
13
Location
sw Florida
The answer is no. What Peter is getting at, is the 1000 million Dollar question. Did you disconnect from the the grid? That determines what you need to do. Voltage has nothing to do with you question. And how did you disconnect it?
Please see updated pics in reply.
 

peapvp

Well-known member
Steel Soldiers Supporter
1,159
1,344
113
Location
Basehor, KS
77B66C5D-1F52-4B6B-AFB9-4D8305B34EE3.jpeg

More questions:

1. The incoming Neutral cannot be left connected because they run straight out to pole

2. can you pull meter?

3. Can this box be locked with a pad lock?

4. what happened to your incoming utility power pole / transformer?

5. Does your house have a green wire on each outlet for earth grounding or is this a two wire Phase Neutral no ground wire installation from back in the day?
 

Islandfarmer

Member
22
31
13
Location
sw Florida
View attachment 881694

More questions:

1. The incoming Neutral cannot be left connected because they run straight out to pole

2. can you pull meter?

3. Can this box be locked with a pad lock?

4. what happened to your incoming utility power pole / transformer?

5. Does your house have a green wire on each outlet for earth grounding or is this a two wire Phase Neutral no ground wire installation from back in the day?
1.
Disconnected now.

2.
No

3.
Yes once I'm done.

4.
Nothing, it's fine.
Power poles broke off on the main feeder line by the road about 3 miles away.

5.
Yes, it's a 2 wire phase + neutral.20221011_132107.jpg20221011_132107.jpg
 
Last edited:

Guyfang

Moderator
Staff member
Moderator
17,492
25,873
113
Location
Burgkunstadt, Germany
Then you are NOT disconnected from the grid.

Yes, someone can answer your questions about the Neutral bod, but the answer could only be formed after you supplying additional info.
 

peapvp

Well-known member
Steel Soldiers Supporter
1,159
1,344
113
Location
Basehor, KS
They're all replied to.
Great, this bonds the generator neutral to its chassis and your ground rod.
This is your current main bond and the only bond since you have no ground wires inside your breaker panel

Your Generator is going to fall off the pallets!! Move the Generator to the Ground where it can sink in if the ground is still soaked

Tape off the incoming Neutral in the box!!!!!
Lock the Box!!!!!

Pull The Meter if at all possible!!!!

You have to be completely off Grid before you can proceed!!!!!



0DBCC524-B4F9-4C32-BB3D-51B4BF53B594.jpeg
 
Top