• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

What do i need to auto start my mep803a?

spotrep

Active member
78
129
33
Location
Texas
Which do you recommend?
I know this question wasn’t for me but I’ll jump in.

If your panel has a 200 amps breaker in it, you either need a service rated ATS, or you will need to install a separate 200 amp breaker.

The reason for this is that you need to be able to disconnect power in front of your ATS Generac offers both service entrance rated and not service entrance rated.

The ASCO 165 looks like a 2-wire start ATS. Check the enclosure to ensure it’s rated for installation outside if that’s where you plan on installing it (it doesn’t appear to be to me). This ATS may be the more economical option as it doesn’t require Kurt’s more expensive controller (he’ll jump in to correct me if I’m wrong). But you need to include the cost of a seperate breaker and keep in mind it may need to be mounted indoors.

I think the Honeywell is a rebranded generac, but can’t know for sure without a model no.

EDIT-

just for clarity regardless of if your panel has a breaker in it or not you will need to put a breaker in front of your ATS. If you breaker is separate from your panel will reuse that breaker. If your service breaker is apart or your panel you will need to purchase a seperate 200 amp breaker, or buy a service rated ATS, which itself will have a 200 amp (or whatever service you need) breaker for service disconnect.
 

HDJ81MAX

New member
27
18
3
Location
Homestead, Florida
I know this question wasn’t for me but I’ll jump in.

If your panel has a 200 amps breaker in it, you either need a service rated ATS, or you will need to install a separate 200 amp breaker.

The reason for this is that you need to be able to disconnect power in front of your ATS Generac offers both service entrance rated and not service entrance rated.

The ASCO 165 looks like a 2-wire start ATS. Check the enclosure to ensure it’s rated for installation outside if that’s where you plan on installing it (it doesn’t appear to be to me). This ATS may be the more economical option as it doesn’t require Kurt’s more expensive controller (he’ll jump in to correct me if I’m wrong). But you need to include the cost of a seperate breaker and keep in mind it may need to be mounted indoors.

I think the Honeywell is a rebranded generac, but can’t know for sure without a model no.

EDIT-

just for clarity regardless of if your panel has a breaker in it or not you will need to put a breaker in front of your ATS. If you breaker is separate from your panel will reuse that breaker. If your service breaker is apart or your panel you will need to purchase a seperate 200 amp breaker, or buy a service rated ATS, which itself will have a 200 amp (or whatever service you need) breaker for service disconnect.

It seems like I can get this honeywell transfer switch locally. He's the model #RXSM200A3. Screenshot_20241118_063709_Facebook.jpg
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks