My problem is supplying the rv with enough amps to run. In 120v 1ph, the 5k will supply 52 amps. In 240v 1ph, it will only supply 26 amps. If I wire it with 4 gauge wire from the genny to the rv sub panel and then slit it off to 2 legs, I think I would be getting more amps.
think about what your saying, 26*2=52, there is no more power. the only difference is if the loads are greatly unbalanced and one side pulls more then 26 amps. generally though the big use items are on either side of the panel.
ultimately if you are sure you will never run anything 240, connecting l1 and l2 in the panel together, you would not need to worry about balancing the loads, simply overloading the generator in general