• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

10kw gen. no power to control panel

Andres_fuze

New member
11
9
3
Location
Fort Irwin, Ca
I got an MEP 803A 10kw gen that was running fine a couple days ago. all of a sudden I got no power to the control panel. any help is appreciated.
Gen cranks from the dead crank switch Btw.
 

pclausen

Well-known member
Steel Soldiers Supporter
452
281
63
Location
Afton, VA
Yep, CB1. Silly question, but you did put the dead crank switch back into NORMAL position and not OFF, right?
 

Guyfang

Moderator
Staff member
Moderator
16,776
24,103
113
Location
Burgkunstadt, Germany
Well, what you really need to do is get the schematic out. Then jamawieb's advice will start you on the road.

Have you downloaded the TM's.
Have you spent a little time going through the Operators TM?
Can you read a schematic?

We need to know this so maybe we can get you started troubleshooting.
 

Andres_fuze

New member
11
9
3
Location
Fort Irwin, Ca
Did you check to be sure the red Emergency Off button is pulled out?
Yes I did
Well, what you really need to do is get the schematic out. Then jamawieb's advice will start you on the road.

Have you downloaded the TM's.
Have you spent a little time going through the Operators TM?
Can you read a schematic?

We need to know this so maybe we can get you started troubleshooting.
i can read the schematic!
 

kloppk

Well-known member
Steel Soldiers Supporter
2,145
3,526
113
Location
Pepperell, Massachusetts
For starters I'd suggest using your meter and see if there is 24 volts DC present on each of the terminals of the Emergency off switch.
If present then check each of the terminals on CB1.
If present then check S1 terminals 2,4,6 & 8.
If present then put S1 in the Prime/Run position and again check for 24 volts DC at S1 terminals 2,4,6,8.

Let us know what you get for readings.
 

Andres_fuze

New member
11
9
3
Location
Fort Irwin, Ca
For starters I'd suggest using your meter and see if there is 24 volts DC present on each of the terminals of the Emergency off switch.
If present then check each of the terminals on CB1.
If present then check S1 terminals 2,4,6 & 8.
If present then put S1 in the Prime/Run position and again check for 24 volts DC at S1 terminals 2,4,6,8.

Let us know what you get for readings.
Got 24vdc on the red
I’m getting nothing on Cb1 when pushed in and out. I switched that out today as wellimage.jpg
 
Last edited:

Andres_fuze

New member
11
9
3
Location
Fort Irwin, Ca
For starters I'd suggest using your meter and see if there is 24 volts DC present on each of the terminals of the Emergency off switch.
If present then check each of the terminals on CB1.
If present then check S1 terminals 2,4,6 & 8.
If present then put S1 in the Prime/Run position and again check for 24 volts DC at S1 terminals 2,4,6,8.

Let us know what you get for readings.
Where do those red and blue wires go to after they leave the top of the picture? Those are not in a normal 803.
thank you for pointing that out😂 it’s all good now, the gen is inside a CK and I guess there’s a emergency stop switch inside the Ck that those wires run to
 

Ray70

Well-known member
2,595
5,914
113
Location
West greenwich/RI
Does that 803 also have non-standard auxiliary wiring going to the gages and is your data plug sitting inside the control box wrapped in bubble wrap, with a remote monitoring plug in place of the data port?
If so, I don't think you can operate the machine without the "Jumper" cap screwed into the remote monitoring plug.
otherwise, just remove the whole setup and put it back to original, it only takes like 15 minutes to remove everything.
 

Guyfang

Moderator
Staff member
Moderator
16,776
24,103
113
Location
Burgkunstadt, Germany
The Mod Ray is talking about was supposed to be for something, at the time I saw it, for a confidential system. A Fire Finder system. When its hooked up to the Container Kitchen, I think it had a different hook up system. I would like to see pictures of the compleat control panel, inside. Please.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks