Hey all, I've recently received an 802a and it won't release the fuel stop solenoid or attempt to crank from the front panel.
If I put the switch on either prime position it runs the corresponding fuel pump.
If I try to start it nothing happens.
Enabling/disabling battle short makes no difference.
I have tried cranking/running while depressing the test button and it has no effect.
I have tried depressing/releasing the emergency shutoff button, it appears to operate normally because it disables pumps when depressed, and allows when out.
However if I manually retract the fuel stop solenoid (and zip tie it in the run position) it still won't crank from the front panel. However if I then use the internal bypass switch it will crank, fire and run just fine. It will produce power, none of the error/warning lights illuminate, I can use it, tune freq and voltage, gauges read good, temp reads reasonable. However if I cut my zip-tie the fuel cut off solenoid returns to closed and kills the motor.
So my ASSUMPTION is that there is a sensor/system that is telling the generator it is NOT ready to start, so it will not power up/retract the fuel stop solenoid and will not allow the starter to engage from the front switch.
My ASSUMPTION is that if it was just the fuel stop solenoid, it would still attempt to crank and physically operating it would enable it to start and run from the front switch.
There is oil and no oil warning light illuminated.
There is fuel and no fuel warning light illuminated.
There is coolant and no temp light illuminated.
All 4 warning lights do illuminate when pressing test button.
Any advice, even if it is a link to a section of a TM for troubleshooting and where to to start would be much appreciated!
This unit has the version 3 switches on it if that makes any difference. I will happily provide any pictures/video if anyone thinks it would help, figured this problem was easier to describe then video
TIA ya'll!
PS: If anyone happens to live in/around the Austin TX area will trade food for hands on knowledge!
If I put the switch on either prime position it runs the corresponding fuel pump.
If I try to start it nothing happens.
Enabling/disabling battle short makes no difference.
I have tried cranking/running while depressing the test button and it has no effect.
I have tried depressing/releasing the emergency shutoff button, it appears to operate normally because it disables pumps when depressed, and allows when out.
However if I manually retract the fuel stop solenoid (and zip tie it in the run position) it still won't crank from the front panel. However if I then use the internal bypass switch it will crank, fire and run just fine. It will produce power, none of the error/warning lights illuminate, I can use it, tune freq and voltage, gauges read good, temp reads reasonable. However if I cut my zip-tie the fuel cut off solenoid returns to closed and kills the motor.
So my ASSUMPTION is that there is a sensor/system that is telling the generator it is NOT ready to start, so it will not power up/retract the fuel stop solenoid and will not allow the starter to engage from the front switch.
My ASSUMPTION is that if it was just the fuel stop solenoid, it would still attempt to crank and physically operating it would enable it to start and run from the front switch.
There is oil and no oil warning light illuminated.
There is fuel and no fuel warning light illuminated.
There is coolant and no temp light illuminated.
All 4 warning lights do illuminate when pressing test button.
Any advice, even if it is a link to a section of a TM for troubleshooting and where to to start would be much appreciated!
This unit has the version 3 switches on it if that makes any difference. I will happily provide any pictures/video if anyone thinks it would help, figured this problem was easier to describe then video
TIA ya'll!
PS: If anyone happens to live in/around the Austin TX area will trade food for hands on knowledge!