Okay, so I pulled the top cover off today to start digging. Everything looks fairly clean & noting obviously loose. It appears as if the coil lead wires going up to TBS have been messed with before making me think that someone has gone through the same tests that I am about to.
View attachment 761336
Did some searching on the forum & came up on this thread where someone had an issue with one leg putting out the wrong voltage.
https://www.steelsoldiers.com/showthread.php?180607-MEP-802A-voltage-readings-not-right
I first started with the voltage regulator testing... Section 2-27-2 of TM 9-6115-641-24, page 95 of .pdf file. All was within what it should be. I was a bit confused by step o... "o. If steps h. j, I and n are as Indicated above, AC voltage regulator IS defective and must be replaced" If they're as indicated above, then why does it need to be replaced? I'm guessing it is a typo & should say NOT as indicated above. Am I just being dumb?
I moved on to testing generator stator... Section 4-10-7 of TM 9-6115-641-24, page 221 of .pdf file. It has you reference table 4-1 at the beginning of the 4-10 section on page 217 of the .pdf file. The range on the stator leads should be between .3731 & .5047. Step g said to use a resistance bridge... I don't know what this is. The resistance I got between all the wire pares was .6 with both of my multimeters. This is high, but I don't know how to make my meters show a more accurate reading. When I change the setting, it gives me all zeroes. Tried with two good multimeters. Maybe me being dumb again? Moving to step h... I got a reading of 2.2. This is much higher than it should be. Steps j & k are good.
So, according to step i, the stator winding is open & must be replaced.
Please tell me I'm wrong!
I'm not sure what to test next.. or if there is anything else to even test.
After getting to this point, I stopped & typed this up. If the stator is bad...