David,
I'm sorry that cleaning up the magnets and fixing the bare wire didn't solve your problem. One thing the tests in the TM do not check for is insulation breakdown. That is obviously what you have going on with your stator. The Ohm readings show up good, and the readings to ground show up good, but as soon as you start putting some amperage through it, the insulation must be breaking down and basically shorting out part of the coils. The only way to test for that is with a Meggar, most people in the general public don't have one of those. Luckily for me, I'm not most people...LOL
Good luck with your new stator and check back in with us and let us know how it works out.
I'm sorry that cleaning up the magnets and fixing the bare wire didn't solve your problem. One thing the tests in the TM do not check for is insulation breakdown. That is obviously what you have going on with your stator. The Ohm readings show up good, and the readings to ground show up good, but as soon as you start putting some amperage through it, the insulation must be breaking down and basically shorting out part of the coils. The only way to test for that is with a Meggar, most people in the general public don't have one of those. Luckily for me, I'm not most people...LOL