On the AVDR 054 the connection between A + C is the AC Voltage Sense Input and can be between 170 VAC to 520 VAC
the connection between B + C is the AC power supply and should be between 170VAC and 300VAC max
i left the B connection open in my wiring diagrams on purpose.
please check the AVDR 054 manual for connecting A, B and C to match your Genset setup for Voltage and Phases
The system as drawn will not provide VR functionality after excitation until B is connected as per AVDR Manual
Thank You
the connection between B + C is the AC power supply and should be between 170VAC and 300VAC max
i left the B connection open in my wiring diagrams on purpose.
please check the AVDR 054 manual for connecting A, B and C to match your Genset setup for Voltage and Phases
The system as drawn will not provide VR functionality after excitation until B is connected as per AVDR Manual